jjdh

Member
The problem is lightning storms are toasting the pump motors.

The post mounted pool panel has a feeder with an EGC. The EGC bar is connected to a ground rod at the pool panel, but has no connection to the EPG.

Does a post mounted swimming pool panel have to be connected to the EPG?

During a storm is'nt the EPG acting as a means to disipate any lightning strikes?
 
Last edited:
The EPG is connected to the EGC through the ground wire in the pool pump circuit. Maybe this is why the motors are taking the hit? :-?

While it is not required to connect any additional jumpers between the EPG and the EGC, it may be in your best interest in this case to do so.
 