swimming pool service call
bob j
I was wondering if anyone had any input on the following situation. I received a service call regarding a swimming pool pump motor. The pool was installed earlier this summer,has been used regularly, everything has run fine. It has a 2 hp. rated motor running off a 20 amp circuit with a Qo gfci breaker in the panel. The length of the circuit looks to be about 100 feet. Recently it has been running for about 20 minutes before the breaker will trip. Possible voltage drop issue? Gfci breaker problem ? Anyone have any thoughts ?
Try this as a temporary experiment:
Replace the GFCI breaker with a standard one, and wire in a GFCI breaker (the same one would be even more telling) in a small 2-ckt enclosure at the motor.
Even easier, or first, use a clamp-on ammeter at the breaker and see if the current is higher than it should be. The odd are that it's moisture infiltration, though.
Centrifugal pumps draw more current when they pump more water. If there is something that is causing it to pump more water (added nozzles, nozzle of the pipe allowing more flow) or an impeller on a plastic pump that is dragging, it will cause more current to be drawn.
swimming pool prt 2
swimming pool prt 2
Mr. Fine , you're living up to your name.Checked out this call on Friday 9/19-diagnosis-small nick in the conductor insulation with a side of moisture infiltration.The motor was rated 2 hp. 15 amp 115 volts. Voltage drop was no issue, at the motor I had 120 volts. Amperage was consistently around 13.5 amps. Originally I suspected the gfi breaker , and replaced it with a regular 20 amp for test purposes- it held all day long. Not enough to trip a regular breaker, but enough current bled off to trip a gfi.Thanks for the insight.:smile:
I megohm meter would have found this in about 2 minutes flat. Pool pumps, fountain pumps, and pumps of any sort; break out the megger.
Thanks for the advice.Is my understanding of what a megger does correct? Doesn't it induce a small voltage into a conductor to determine its integrity? Can you recommend a good one that won't break the bank, since i'll probably run into this situation again?
Actually, it pushes a pretty big voltage. Check neutral to ground and hot to ground (or each hot to ground, if 240). Chances are that would have showed something right away, and saved you hours of troubleshooting.
I guess I've been recommending the Supco M-500 and the Extech 380260 for dirt simple, cheap megohm meters for troubleshooting type testing. They each around 100 bucks.
Hey Marc, I have the 380260, and was wondering what readings would be questionable or 'no go' on say a wire or a motor windong? All the wire pulls I have done go to infinity, but would like to know when I should classify something as not good any more.
~Matt