They didn't derate the switch. It is good for 100% of its rating, the 80% is for motor switching not general lighting. Not all lighting is considered continuous, you would have to make that determination at a per installation basis.Originally posted by jeff43222:
...they derated the ampacity of the switch since you really aren't supposed to have more than 80% of 20A running through the switch.
Good question! I am inclined to think not. The load considerations for cord-and-plug equipment are taken into account with the receptacle load. Someone might say that any given receptacle load might be on for more than 3 hours, and they might site a reading lamp as an example. I would counter by suggesting that the 180 VA per receptacle is based on a ?real? load of 144 VA, and that 25% has already been added to that number, thus bringing the total to 180. In any event, I see nothing in the code that would lead me to add 25% to receptacle loads.Originally posted by bphgravity: Also, do cord-and-plug connected loads get counted into continuous loading?