hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
I have an inspector who by most is a very fair inspector as far as not calling things that are not in the NEC. But he has hit me with a box fill problem that just don't add up. And maybe I'm getting it wrong but I'd like to be sure before I talk to him.
Ok here's what it's about
I have a two-gain plastic switch box the listed size is 34.4 cubic inch's This should allow for 16 #14awg wires. we have 3-14/3 NM's and two 14/2 NM's entering the box. with two switch's one 3-way and one 4-way that will be mounted in this box.
ok from what I think I know is we have a total of 13 wires and one ground that can be counted. Now 314.16(B)(1) exception allows us to exempt the grounding conductor. now 314.16(B)(4) requires us to deduct 2 wires for each device yoke that will be mounted in the box from the allowed number of conductor's. this bring's us to 12 allowed wires. Now this is what is confussing:
Ok here's what it's about
I have a two-gain plastic switch box the listed size is 34.4 cubic inch's This should allow for 16 #14awg wires. we have 3-14/3 NM's and two 14/2 NM's entering the box. with two switch's one 3-way and one 4-way that will be mounted in this box.
ok from what I think I know is we have a total of 13 wires and one ground that can be counted. Now 314.16(B)(1) exception allows us to exempt the grounding conductor. now 314.16(B)(4) requires us to deduct 2 wires for each device yoke that will be mounted in the box from the allowed number of conductor's. this bring's us to 12 allowed wires. Now this is what is confussing:
Does this mean that the wires that terminate on the 3-ways and 4-ways since they dont leave the box can be deducted from the count? Or is the inspector correct.314.16(B)(1)(last sentance) A conductor, no part of which leaves the box, shall not be counted.