Switch can’t turn off

ccrosland

Member
Location
Colorado
Occupation
Journeyman Electrician
I’m having some issues with the dimmer switches on my job and nobody can figure it out. I’ve talked to multiple journeyman, lighting engineers, and product manufacturers without any answers. I have 12 paddle dimmer switches each controlling a single 2x4 led panel on a 277v circuit. Switches and drivers are rated for 120-277v 0-10 dimming. Every time I install a switch, it reads ~100v from the switch leg to ground when the switch is turned off. It allows the full 277v through when turned on. There is no continuity between the hot and switch leg when I ring it out. If I connect only the hot and ground to a new switch, no dimmers or load, the switch still fails and lets ~100v through. If I replace the dimmer switch with a non dimming toggle switch, it functions correctly. It turns on and off and shorting the dimmer leads dims the lights. Has anyone seen this before?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What are you testing it with a DMM? I would bet that if you used a solenoid type tester like a Wiggy you would see that there is no voltage present with the switch off.

Welcome to the Forum. :)
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
I have 12 paddle dimmer switches each controlling a single 2x4 led panel on a 277v circuit. Switches and drivers are rated for 120-277v 0-10 dimming. Every time I install a switch, it reads ~100v from the switch leg to ground when the switch is turned off. It allows the full 277v through when turned on.
But the big question is- does the light function properly??

-Hal
 

ELA

Senior Member
Occupation
Electrical Test Engineer
Switches and drivers are rated for 120-277v 0-10 dimming.
What have you done with the 0-10V dimming control input? Do the dimmers have a configuration setting to enable/disable the 0-10V dimming function?
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Every time I install a switch, it reads ~100v from the switch leg to ground when the switch is turned off.
Not understanding this. Why are you measuring from the switch leg to ground? With the dimmer off what do you measure from the switch leg to neutral? With the dimmer on I assume the fixture lights because you say you get 277. But with the dimmer off does the fixture light or what? All you talk about is the 100V and not the actual problem.

-Hal
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Not understanding this. Why are you measuring from the switch leg to ground? With the dimmer off what do you measure from the switch leg to neutral? With the dimmer on I assume the fixture lights because you say you get 277. But with the dimmer off does the fixture light or what? All you talk about is the 100V and not the actual problem.

-Hal
He said the lights don't turn off.
 