I'm looking into retrofitting a natural gas compression skid for Class I Div 2 and I need to clear up some doubts I have about an existing switch gauge on the skid.
Here's the current gauge(it's the SDB500, not the XP model): http://www.fwmurphy.com/uploaded/documents/pdfs/7543.pdf
I checked with the manufacturer and the current gauge is not listed for CID2. Being that this gauge has an internal switch, I believe it qualifies as a switch under 501.105(B)(2) and does not meet any of the exceptions. Is this correct? If so, I'll be replacing it with the XP model and it seems that I'll also need a conduit seal between the gauge and the skid's terminal box.
For context:
The switch gauge sends a shutdown signal to the control panel via a 12VDC signal. The control panel will be mounted in an unclassified area. All conduit on the skid is threaded steel and the enclosure for the wiring terminals on the skid will be NEMA 4 as it isn't required to be XP.
For context: