Switch legs and 300.3(b)

Pinnie

Senior Member
Location
Ohio
Occupation
Commercial Electrician
Does 300.3(b) make it so you need neutrals with the associated hots in every raceway? I have a switch bank with conduit ran to it, which exempts you from needing a grounded conductor at your switch bank (404.2(c)(1))
 
No. Somewhere in 300.3(b) it says "and where needed, the grounded conductor".
Gotcha. I thought there was a chance that alluded to three phase loads.

Can someone also explain the nuances of the egc and ungrounded conductors canceling out magnetic induction or self impedance during a fault?
 