mstrlucky74

Senior Member
Location
NJ
Just curious as to how others would wire this? So the lights are all on one circuit. So I know you could bring the circuit/power to either the lights or to the switch but normally you would bring the power to the switch. So the F5's are controlled by one switch and the F7 by the other. So you need a separate switch leg from each switch. Would you run (2) 12/2 from each switch? Thanks.
 

Attachments

  • InkedCapture_LI.jpg
    InkedCapture_LI.jpg
    120.6 KB · Views: 0

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Generally, with cables, 12-2 to switches, 12-2's to each light group, as you said.

With conduit, J-box above switches, only feed and two legs down, neutral feed through.

Your switches have a D by each S. Dimmers? Another reason for neutral at switches.
 

mstrlucky74

Senior Member
Location
NJ
Generally, with cables, 12-2 to switches, 12-2's to each light group, as you said.

With conduit, J-box above switches, only feed and two legs down, neutral feed through.

Your switches have a D by each S. Dimmers? Another reason for neutral at switches.

Yes dimmers.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It also depends on how the rest of the job is wired; you generally match existing.

Yes dimmers.
Then I would do one of what I said above, but add a neutral to the conduit.

Of course, you need a suspended ceiling to use junction boxes.
 