switch loop-marking grounded wire
section 404.2(A) states that all switching shall be done only in the ungrounded circuit conductor for 3/4-way swithcing.
Where in the code does it talk about the marking of the neutral, used as a switch leg, for a single pole switch?
any help would be appreciated
Re: switch loop-marking grounded wire
Mac, think of it, not as "using the neutral", but more as "using the white wire".
200.7(C)(2) is another code requirement that the state of Massachusetts has revised to read as follows...
200.7(C)(2)Revise the last sentence to read as follows:
In these applications reidentification of the conductor with white or gray insulation or with three white stripes shall not be required.
If these DIYers don't understand the long used practice of useing the white wire for an ungrounded conductor in a switch loop, then they shouldn't be in there in the first place...
shortcircuit2
did i read that right? there is no need to re identify the white conductor if it is the return from the switch, only if it is the supply to the switch.
JbWhite, You cannot use the white as a return from the switch, whether or not you re-identify it. It can only be re-identified and used to feed the switch, not to return.