Switch question

Status
Not open for further replies.

defishu

Member
Location
new york
A stupid question, how to know if a disconnect switch can be used to multi panels or just one single panel. Does it show something like poles inside that we can determine? More detail will be appreciated!
 
Not sure I follow your question. Please give all of the pertinent details. What are you trying to do, at what voltage / phase / current, under what conditions etc. etc. etc.

"Switch" is not a very descriptive term, even "disconnect switch" is not that much more helpful. There are literally hundreds of different kinds out there.
 
defishu:

What I interpret from your post is that rather than having one disconnect controlling one feeder circuit that goes to multiple panels you are looking for a switch with enough independent poles that you can interrupt all the hot leads of several independent circuits.
If that is the case, and if you are thinking of the knife switch type units in an enclosure with an external operating handle, I do not know of any that routinely offer more than just 2 or 3 poles for one single phase or three phase circuit.
 
Not sure I follow your question. Please give all of the pertinent details. What are you trying to do, at what voltage / phase / current, under what conditions etc. etc. etc.

"Switch" is not a very descriptive term, even "disconnect switch" is not that much more helpful. There are literally hundreds of different kinds out there.
887621872410.jpgdoes this one mean we can have a maximum of 6 fuses, and each of them can handle a panel or feed the equipment?
 
Square D has four and six pole "Safety switches" in their catalog.

Don't really know if there is a specific intended use for them though, never seen one in the wild either.
 
Square D has four and six pole "Safety switches" in their catalog.

Don't really know if there is a specific intended use for them though, never seen one in the wild either.

4P used for where you need to switch the neutral, such as a hazardous location.
6P used as motor disconnect for a two speed, two winding. Used several of em back it the day before VFD's were common.

MTW
 
4P used for where you need to switch the neutral, such as a hazardous location.
6P used as motor disconnect for a two speed, two winding. Used several of em back it the day before VFD's were common.

MTW
You wouldn't be allowed to put fuses in the neutral in a fused disconnect - solid jumper could be used I guess, and have even seen that on corner grounded delta systems.

Another thought though not many encounter it is two phase systems.
 