mstrlucky74
Senior Member
- Location
- NJ
Looking for help on how I would size the following: Boy I gotta learn some electrical sizing formulas.
120/208 4000A switchboard and I need to feed a 120/208v 3 phase 200A motor. It would be a continuous load? How would I go about sizing the switch in the switchboard? Would it be 125% of the 200A? I think I need a disconnect by the motor so I'd be sizing to the disconnect.
Same switchboard and I need to feed a 120/208v 3 phase 300A panel. How would I go about sizing the switch in the switchboard?
Ok, now a tricky one(for me at least). I want to feed a 120/208 1200a dist board from the 120/208v 4000a board but want to feed it via 277/480. So I'd need a step up xfrmr by the 4000a board then a step down xfrmr by the 1200a board. How would I go about sizing the switch in the 4000A board and the two xfrmrs.
I know this is a alot and appreciate any feedback/overview on how to approach these questions on sizing.
So when sizing, equipment and conductors and you know the size of the load do you then size the OCPD then the feeder?
120/208 4000A switchboard and I need to feed a 120/208v 3 phase 200A motor. It would be a continuous load? How would I go about sizing the switch in the switchboard? Would it be 125% of the 200A? I think I need a disconnect by the motor so I'd be sizing to the disconnect.
Same switchboard and I need to feed a 120/208v 3 phase 300A panel. How would I go about sizing the switch in the switchboard?
Ok, now a tricky one(for me at least). I want to feed a 120/208 1200a dist board from the 120/208v 4000a board but want to feed it via 277/480. So I'd need a step up xfrmr by the 4000a board then a step down xfrmr by the 1200a board. How would I go about sizing the switch in the 4000A board and the two xfrmrs.
I know this is a alot and appreciate any feedback/overview on how to approach these questions on sizing.
So when sizing, equipment and conductors and you know the size of the load do you then size the OCPD then the feeder?