I think I asked this question before, anyway, I hope someone can have more detailed answers for me this time:
We plan to have 4,000A service switchboard (480V/3PH, 4W+G) serving healthcare facility. This switchbaord shall have 4,000A main and below branches:
3,000A
1,600A
1,000A
800A
(2) 400A
(2) 250A
The owner wants to have main and all branch feeder protections in main switchboard to be fused switches , no breaker is allowed.
Any panels downstream of main switchboard, they are okay to go with breakers. My understanding is we need to comply with NEC article 517 for two levels of ground fault protection rule. How do we specify fused switch to comply with NEC and satisfy above owner's desire? Any detailed recommendations shall be great appreciated especially con and pros of CB using vs. fused switches.
We plan to have 4,000A service switchboard (480V/3PH, 4W+G) serving healthcare facility. This switchbaord shall have 4,000A main and below branches:
3,000A
1,600A
1,000A
800A
(2) 400A
(2) 250A
The owner wants to have main and all branch feeder protections in main switchboard to be fused switches , no breaker is allowed.
Any panels downstream of main switchboard, they are okay to go with breakers. My understanding is we need to comply with NEC article 517 for two levels of ground fault protection rule. How do we specify fused switch to comply with NEC and satisfy above owner's desire? Any detailed recommendations shall be great appreciated especially con and pros of CB using vs. fused switches.