I have been asked by my companies Director of Customer Service to research the NEC concerning the following situation.
One of our field engineers was sent to a customers plant to replace the main disconnecting means (molded case switch)on an induction heating power supply. This main disconnecting means was fed from wires coming from an upstream switchboard containing several switches and/or manually operated circuit breakers that supplied power to other machines, etc. The switch that provided power to the induction heating power supply was shut off but apparently there was no provision on the switch for locking it in the off position. A piece of tape was placed over the switch by the customer when they shut off the switch and our field engineer was informed that the switch was shut off and it was now safe to replace the molded case switch in the induction heating power supply. Our field engineer tried to explain that this was not a safe practice and the customer insisted that he continue with the repair.
I have read NEC section 408 in it's entirety as well as the referred to sections in 408.2 (Articles 240, 250, 312, 314, 404) but do not find anything stating that a switch in a switchboard must have a provision of being lockable in the off position.
I have also read NFPA 79 and specifically section 7 covers Supply circuit disconnecting means. Article 7.10.3 states "The operating handle shall be capable of being locked only in the open (off) position." Is your interpretation of this that this applies to the switchboard containing the switch supplying power to our induction heating power supply and that the switch in the switchgear must be able to be locked out in the off position?
I have also read OSHA standards 1910.147 regarding the control of hazardous energy (lockout/tagout) and it seems to indicate that it is permissible to use a tagout procedure instead of a lockout procedure if the energy isolating device is not capable of being locked out (1910.147(c)(2)(i). Also is states that after January 2, 1990 when a repair or replacement is done to a machine or equipment the energy isolating devices that are installed shall be designed to accept a lockout device. 1910.147(c)(2)(iii). I am not sure when the switchgear in question was installed but I was told it did not have provision for a lockout.
Is the scenario described above in violation of code requirements or is this an acceptable method for shutting down a piece of equipment to allow repairs?
Thank you in advance for your help,
John
One of our field engineers was sent to a customers plant to replace the main disconnecting means (molded case switch)on an induction heating power supply. This main disconnecting means was fed from wires coming from an upstream switchboard containing several switches and/or manually operated circuit breakers that supplied power to other machines, etc. The switch that provided power to the induction heating power supply was shut off but apparently there was no provision on the switch for locking it in the off position. A piece of tape was placed over the switch by the customer when they shut off the switch and our field engineer was informed that the switch was shut off and it was now safe to replace the molded case switch in the induction heating power supply. Our field engineer tried to explain that this was not a safe practice and the customer insisted that he continue with the repair.
I have read NEC section 408 in it's entirety as well as the referred to sections in 408.2 (Articles 240, 250, 312, 314, 404) but do not find anything stating that a switch in a switchboard must have a provision of being lockable in the off position.
I have also read NFPA 79 and specifically section 7 covers Supply circuit disconnecting means. Article 7.10.3 states "The operating handle shall be capable of being locked only in the open (off) position." Is your interpretation of this that this applies to the switchboard containing the switch supplying power to our induction heating power supply and that the switch in the switchgear must be able to be locked out in the off position?
I have also read OSHA standards 1910.147 regarding the control of hazardous energy (lockout/tagout) and it seems to indicate that it is permissible to use a tagout procedure instead of a lockout procedure if the energy isolating device is not capable of being locked out (1910.147(c)(2)(i). Also is states that after January 2, 1990 when a repair or replacement is done to a machine or equipment the energy isolating devices that are installed shall be designed to accept a lockout device. 1910.147(c)(2)(iii). I am not sure when the switchgear in question was installed but I was told it did not have provision for a lockout.
Is the scenario described above in violation of code requirements or is this an acceptable method for shutting down a piece of equipment to allow repairs?
Thank you in advance for your help,
John