MCC Rooms that have metal flooring are considered to have the same potential and matting is not required. Does this apply when the metal floor is painted and often dirty?
that may be a local law or specific to some of the buildings you work in, there is no NEC requirement for it though. Both metal floors and concrete floors are conductive.