I am installing some equipment and am trying my best to make sure it meets code. With respect to my residential switchboard (I assume this can also be referred to sa a breaker panel), I am stuck at NEC 408.36.EXC 2 & 3
Exception No. 2: Individual protection shall not be required
for a panelboard protected on its supply side by two
main circuit breakers or two sets of fuses having a combined
rating not greater than that of the panelboard. A
panelboard constructed or wired under this exception shall
not contain more than 42 overcurrent devices. For the purposes
of determining the maximum of 42 overcurrent devices,
a 2-pole or a 3-pole circuit breaker shall be considered
as two or three overcurrent devices, respectively.
Exception No. 3: For existing panelboards, individual protection
shall not be required for a panelboard used as service
equipment for an individual residential occupancy.
EXC 2: First, what is meant by "individual protection"? Second, Does this mean that if I put a 2-pole beaker in as main on a breaker panel, I can only have 42 branch breakers (assuming ALL are 1-pole)?
EXC 3: I don't understand this at all. This makes it sound like I don't even need breakers or fuses. All I need is the main breaker.
Can someone please help me understand this?
Thanks.
Exception No. 2: Individual protection shall not be required
for a panelboard protected on its supply side by two
main circuit breakers or two sets of fuses having a combined
rating not greater than that of the panelboard. A
panelboard constructed or wired under this exception shall
not contain more than 42 overcurrent devices. For the purposes
of determining the maximum of 42 overcurrent devices,
a 2-pole or a 3-pole circuit breaker shall be considered
as two or three overcurrent devices, respectively.
Exception No. 3: For existing panelboards, individual protection
shall not be required for a panelboard used as service
equipment for an individual residential occupancy.
EXC 2: First, what is meant by "individual protection"? Second, Does this mean that if I put a 2-pole beaker in as main on a breaker panel, I can only have 42 branch breakers (assuming ALL are 1-pole)?
EXC 3: I don't understand this at all. This makes it sound like I don't even need breakers or fuses. All I need is the main breaker.
Can someone please help me understand this?