Remember, AIC is interrupting rating, for OCPD's. Equipment that doesn't interrupt has a SCCR. Are you referring to the SCCR of the panel board/switchboard, or the AIC of the breakers in the equipment?Suppose I have a switchboard rated at 2500A and a panelboard rated 800A both are 100kAIC. Would having them be 200kAIC change the dimension? Would they have to become bigger? Thanks
Oops, just realized that what I said was wrong. Yes I mean SCCR, wish I could change the thread title lolRemember, AIC is interrupting rating, for OCPD's. Equipment that doesn't interrupt has a SCCR. Are you referring to the SCCR of the panel board/switchboard, or the AIC of the breakers in the equipment?
Thanks for your input. Lets add kAIC to the mix: How about 100kAIC and 100kSCCR fully rated panel compared to 200kAIC and 200kSCCR fully rated panel? Would the size change?I am not positive, but i don't think dimensions would change. I know some equipment is actually rated 200k by default. Siemens panel boards appear to come with a 200k SCCR standard, I just looked at one the other day and noticed it. This was just a "standard" 208Y/120 factory PB with 10kaic branch breakers.
I have never had to use or procure an OCPD over 65kaic, and there are probably others with more experience with larger and high AIC/SCCR equipment, but I dont recall ever seeing physical sizes increase with higher AIC. For example, your typical plug on miniature CB is available in 65k versions and it's the same size.Thanks for your input. Lets add kAIC to the mix: How about 100kAIC and 100kSCCR fully rated panel compared to 200kAIC and 200kSCCR fully rated panel? Would the size change?
At my old firm, I've seen 100kAIC being thrown around all the time. It is the downstream panels after the main distribution board where they specify 65kAIC or below for circuit breakers. I wanted to know this because I already have equipment laid out in my plans at 100kAIC, 100kSCCR fully rated. I haven't determined the short circuit current yet from the utility. I was concerned the design would drastically change if the available SCCR came out to be more than 100k.I have never had to use or procure an OCPD over 65kaic, and there are probably others with more experience with larger and high AIC/SCCR equipment, but I dont recall ever seeing physical sizes increase with higher AIC. For example, your typical plug on miniature CB is available in 65k versions and it's the same size.
Sometimes, at 240v we use 480 or 600v OCPD's to get a higher AIC rating. For example one could use a Siemens BQD (the typical 277/480 breaker rated 14k) on a 240 system to get a 65k rating.....or a LGB (65K@480) which would give you 100k at 240. But even that doesn't typically change the size.
I have seen the AIC rating of breakers be limited by their physical size.
Yes.So, just to be specific (and making up numbers):. Say you needed a 600 amp OCPD with a high AIC. Is it plausible that the AIC would not be available in that 600 amp frame size and you would have to go up to the next frame size to get what you need?
Evidently Eaton has some.I have never seen breakers rated for more than 100kAIC.
As Jim D mentioned bracing (of probably same bus) might be the major difference in the switchboard or panelboard.Suppose I have a switchboard rated at 2500A and a panelboard rated 800A both are 100kAIC. Would having them be 200kAIC change the dimension? Would they have to become bigger? Thanks
Learned something new today.Evidently Eaton has some.
https://www.eaton.com › en-us
JGX8200AAG | Eaton Series G complete molded case circuit breaker | Specifications | Eaton
Siemens too. CFD6, is 200k even at 480 volt.Evidently Eaton has some.
https://www.eaton.com › en-us
JGX8200AAG | Eaton Series G complete molded case circuit breaker | Specifications | Eaton
Huh. When I was at Siemens it wasn’t that high. I guess they had to retest to keep up with Eaton.Siemens too. CFD6, is 200k even at 480 volt.
I had a recent job where the utility provided number would have been about 75k. Using actual data it was 60k (both infinite primary). I am not sure what the premium would have been to go to 100K equipment but I assumed it would be a jump so I went through the trouble of getting the equipment data and computing it to see if I can get it below 65.I mostly use AB, Siemens, and Schneider breakers. There is a premium for 65k breakers but it is not as much as it used to be. it used to be it was a big number but the premium has dropped quite a bit over the years. I've never had anybody spec anything over 65k short circuit current rating so I've never had occasion to use breakers rated more than that, but I have seen some in the catalogs as I am leafing through them, but just never used them.