slice

Member
Location
Massachusetts
Hello all I am working on a large residential project and am designing the main switchboard. The load per article 220 is around 600A for each of two meter banks and one house panel. I am planning on supply each with an 800A Circuit breaker in a main switchboard. This switchboard is directly connected to the utility transformer secondary. My question is it allowable to install a 2000A switchboard for the above scenario? I believe it is acceptable since the calculated load is less than 2000A, just the sum of the breakers is larger than the rating (2400A). Also am I correct in that a main breaker is not required for this case (even though the combined breaker ratings exceed the switchboard rating)?
 
Hello all I am working on a large residential project and am designing the main switchboard. The load per article 220 is around 600A for each of two meter banks and one house panel. I am planning on supply each with an 800A Circuit breaker in a main switchboard. This switchboard is directly connected to the utility transformer secondary. My question is it allowable to install a 2000A switchboard for the above scenario? I believe it is acceptable since the calculated load is less than 2000A, just the sum of the breakers is larger than the rating (2400A). Also am I correct in that a main breaker is not required for this case (even though the combined breaker ratings exceed the switchboard rating)?

I am guessing you meant the load was 1600 not 600?

But anyway yes you can use a 2000 amp main lug only switchboard with up to six breakers of any size as long as the calculated load remains under 2000 amps.
 
Status
Not open for further replies.
Top