so this is the dilemma- foreman is repeating your comment. I'm leaning towards what Jim is saying. ABB is unresponsiveConsider the path of current on that vertical bus. You could load the upper and lower portion each to 2000A non-concurrently, because you can't exceed the 3000A horizontal bus.
I don't think I have ever seen vertical section bussing greater than 2000A, except for single devices. Probably time to check the UL standards.so this is the dilemma- foreman is repeating your comment. I'm leaning towards what Jim is saying. ABB is unresponsive