I had made another post but I think it was too confusing. So let me start over.
I have three meter banks in an apt. building with the following loads (they have already had demand factors in table 220.32 applied):
meterbank 1 = 1069A
meterbank 2 = 1079A
meterbank 3 = 857A
total = 3004A
I want to use a horizontal bus switchboard setup with three main breakers serving the three meterbanks.
1) What would the bus need to be rated?
2) If i have the bus rated at 3000A and the 3 main breakers are rated 1200A, 1200A, and 1000A is that code compliant? My problem is that the breaker total is more than the 3000A bus rating so if the breakers all pulled close to their full ratings the bus would be loaded more than 3000A.
3)Can I take the meterbank load totals (before 220.32 demand factors are applied) and use 220.32 on the total combined load for the whole building(the demand factor would be less because a greater number of dwelling units would be included in the calculation)?
I have three meter banks in an apt. building with the following loads (they have already had demand factors in table 220.32 applied):
meterbank 1 = 1069A
meterbank 2 = 1079A
meterbank 3 = 857A
total = 3004A
I want to use a horizontal bus switchboard setup with three main breakers serving the three meterbanks.
1) What would the bus need to be rated?
2) If i have the bus rated at 3000A and the 3 main breakers are rated 1200A, 1200A, and 1000A is that code compliant? My problem is that the breaker total is more than the 3000A bus rating so if the breakers all pulled close to their full ratings the bus would be loaded more than 3000A.
3)Can I take the meterbank load totals (before 220.32 demand factors are applied) and use 220.32 on the total combined load for the whole building(the demand factor would be less because a greater number of dwelling units would be included in the calculation)?