Re: Switched Outlets Coommercial/Residential
Electrojet,
I agree that it is for calculations.
Article 220 is titled Branch-circuit , feeder, and service calculations. If you are calculating the load of a branch circuit in a commercial application you would have to calculate each receptacle at 180 VA minimum.
So if I take a 20 amp circuit (non-continious load) and calculate the load I come up with 13 receptacles allowed on that circuit.
Your original post said "one switch/ckt ???" and the title of the thread talked about commercial and residential.
Ryan is correct about residential.
Chris