Switches near tub

404.4(C) appears unchanged between the 2017, 2020, and 2023 NEC, and it says "Switches shall not be installed within tub or shower spaces unless installed as part of a listed tub or shower assembly."

In contrast, 406.9(C) on receptacles near tubs was expanded in the 2020 NEC.

Cheers, Wayne
 
Is this an issue? Is there a code cycle where it wouldn't have been an issue?

A Man A plan A canal Panama
If it is directly over the tub then it is a violation

404.4
(C) Switches in Tub or Shower Spaces.

Switches shall not be installed within tub or shower spaces unless installed as part of a listed tub or shower assembly.
 
This is from 2008-- I don't know how much further back it goes
404.4 Damp or Wet Locations.

A surface-mounted switch or circuit breaker in a damp or wet location shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2. A flush-mounted switch or circuit breaker in a damp or wet location shall be equipped with a weatherproof cover. Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
 
I thought there was something new/newish about proximity of switches to tubs. Could have sworn I went through this on a job a year or two ago. Maybe I am misremembering. My brain is full. 🧠. I'll have to look up the code wording, but what is the definition of "tub space"? As long as it is not directly above it's okay?
 
This is from 2008-- I don't know how much further back it goes
All I know is my house was built in 1955, and the switch was located outside the bathroom door because it would have been within 1 foot of the edge of the tub. Thinking about that I never located a switch or receptacle within reach of someone in a shower or tub.

And, what's that low voltage for?

-Hal
 
All I know is my house was built in 1955, and the switch was located outside the bathroom door because it would have been within 1 foot of the edge of the tub. Thinking about that I never located a switch or receptacle within reach of someone in a shower or tub.

And, what's that low voltage for?

-Hal
Floor heat
 