drktmplr12
Senior Member
- Location
- South Florida
- Occupation
- Electrical Engineer
I'm tasked with developing the anticipated heat losses in an electrical room as an input to HVAC design.
The Eaton CAG Power Equipment Losses tables seem excessive for low voltage switchgear. I've included heat loss for each breaker and additional loss for each switchgear section. With that I have 17 tons. I still need to include 2700 HP worth of VFD's. The switchgear is rated 5000 A and has 6 sections in use at any given time.
Something doesn't feel right..I understand these are worst case assumptions, bit it seems odd that a switchgear section would give off that much heat even under full load.
Any opinions would be appreciated.
The Eaton CAG Power Equipment Losses tables seem excessive for low voltage switchgear. I've included heat loss for each breaker and additional loss for each switchgear section. With that I have 17 tons. I still need to include 2700 HP worth of VFD's. The switchgear is rated 5000 A and has 6 sections in use at any given time.
Something doesn't feel right..I understand these are worst case assumptions, bit it seems odd that a switchgear section would give off that much heat even under full load.
Any opinions would be appreciated.