Re: Switchgear rating
First my opinion.... Logic indicates that during closed transition for any length of time, there is a possibility of a fault during that period, 6 cycles, 30 cycles, 5 seconds et al. The SWGR should be designed to withstand and interrupt that amount of current coming from both sources.
Then there is the other opinion ..... There is no code or standard that specifically addresses this condition. I argue with my colleagues constantly regarding this issue, as it is almost always an issue, whether it is two utility sources, or the utility and the 'house' generators. Many of my colleagues feel that if it is less than a few seconds, not to consider that case. Some of my other colleagues agree with me.
The applicable code is NEC 110.9. It states that the gear should have a rating sufficient for the nominal circuit voltage and current on the line terminals of the equipment. So the question becomes, what is the available fault current at the line terminals of the equipment? If the fault occurs upstream of the SWGR, then the fault current at the line terminals will be equal to one source's contribution plus any building motor load. If the fault occurs at the tie breaker (or further downstream), the fault current at either line terminal will be equal to one source's contribution.
The catch is what if there is a fault on the line terminal of the equipment. Then you will have both sources and building's motors contributing. What is the likelihood that a fault will occur at the line terminal/bus, or during a few second closed transition?
It is for an engineer/designer to ponder the possibilities.
That's why there is judgment involved in all aspects of this 'stuff'.