Switchgear Section

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Not purchasing this gear and don't have cuts but landing wires on this 5000A drawout breaker. Are you able to tell by the floorplan pic which end of the gear this breaker is located?
 

Attachments

  • Screenshot 2022-12-15 085207.jpg
    Screenshot 2022-12-15 085207.jpg
    69.8 KB · Views: 13
  • Screenshot 2022-12-15 085722.jpg
    Screenshot 2022-12-15 085722.jpg
    134.5 KB · Views: 13
If there is a portable generator connection that is cropped from the oneline you posted, then that would probably be the PG, and the 5000A breakers would be the Master and Gen sections.
 
If there is a portable generator connection that is cropped from the oneline you posted, then that would probably be the PG, and the 5000A breakers would be the Master and Gen sections.
There is a camlock panel that the gear is also feeding. Guess the PG is the breaker for the camlock panel. Pretty impressive pickup on your part.
 
  • Like
Reactions: ron