I've never had to troubleshoot switchgear. It either works or else you have a black crater in the floor where the switch gear used to be. :D

A little more detail might be helpful.
 
Re: SWITCHGEAR TROUBLE SHOOTING

This is not an Electrical Instructor topic, so I am moving it to a different thread where you may find a response. :) Thanks
 
Re: SWITCHGEAR TROUBLE SHOOTING

Well, if you plug a plug tester into receptacles and everything reads okay until someone plugs in a stereo and then you get "Hot/Gnd Reverse" or "Open Neutral" on the plug tester, you might have a loose neutral in your switchgear. Siemens gear sometimes has a "donut" that is easy to forget to tighten, after the sixth time of putting the meter stack on and off the disconnect.

If on the day that the utility comes to hook it up, there is a large puff of smoke and swearing from the gents at the transformer, then you accidentally crossed phases in the disconnect, probably by misidentifying parallel runs.

If it hangs off the wall, the drywall anchors need to be replaced with lags.

Too tight won't hold.

And that's the sum of what I have learned through my own and other's mistakes with switchgear. :)
 
Re: SWITCHGEAR TROUBLE SHOOTING

By the way, please turn off the ALL CAPS feature. It makes the post more difficult to read. It is also considered impolite, as though you were SHOUTING at us.
 
Re: SWITCHGEAR TROUBLE SHOOTING

If you are talking about the big drawout 3000-4000 Amps switchgears, I am not aware of any standards. It is common practice each manufacturer to suply a manual. In addition, they gladly troubleshoot them for about $700-800 per diem.
 