Well, if you plug a plug tester into receptacles and everything reads okay until someone plugs in a stereo and then you get "Hot/Gnd Reverse" or "Open Neutral" on the plug tester, you might have a loose neutral in your switchgear. Siemens gear sometimes has a "donut" that is easy to forget to tighten, after the sixth time of putting the meter stack on and off the disconnect.
If on the day that the utility comes to hook it up, there is a large puff of smoke and swearing from the gents at the transformer, then you accidentally crossed phases in the disconnect, probably by misidentifying parallel runs.
If it hangs off the wall, the drywall anchors need to be replaced with lags.
Too tight won't hold.
And that's the sum of what I have learned through my own and other's mistakes with switchgear.
By the way, please turn off the ALL CAPS feature. It makes the post more difficult to read. It is also considered impolite, as though you were SHOUTING at us.
If you are talking about the big drawout 3000-4000 Amps switchgears, I am not aware of any standards. It is common practice each manufacturer to suply a manual. In addition, they gladly troubleshoot them for about $700-800 per diem.