Derating factors relate to voltage. Because a switching device, such as a simple switch, breaker, contactor, relay, etc., has to open and clear an arc it is much easier to clear AC than DC because AC goes through zero volts 120 times a second. The devices that I'm familiar with have AC voltage ratings that are higher than DC but the current ratings are the same.
So, is you take a switch rated 120vac it most likely will never pass a test for 125vdc. Remember, current is not an issue.
You may have to go it on your own. BUT, to give you a tip that you will say "Gee, I should have thought of that" is to use a 2p switch which doubles the contact gap to clear a DC arc. You can either just loop through the contacts of have one on the + and - side, doesn't matter.
Breakers are used like that all of the time but they do have a DC rating when wired in configuration to 3 poles in series. (Something I be your mother never taught you.
)
But you will still have no
"Official" dc rating if it is not labeled as such.
Dave