malachi constant
- Minneapolis
We have a bunch of single phase motors being installed that require an extra phase wire. The extra phase wire is connected & controlled such that only one of the two phase wires operates at the same time. (If wire 1 is live the motor runs forward, if wire 2 is live the motor runs backward.) Do BOTH these need to be considered current carrying conductors (CCC) for the purposes of 310.15(3)(a) adjustment factors?
I ask because adding the extra wire is a change to the contract. I assume the contractor planned to run home runs to each group of three motors, which would be three CCC per 3/4" home run. If these additional wires are required to be considered CCCs, that would put this at (6) CCCs per home run. The motors are 3/4HP 120V, so FLA of 13.8A each. I don't get into adjustment factors very often, but my understanding of 310.15(B)(2)(b) is "10 or less / 75C" would apply, so derate these by a factor of 1.36. 13.8A x 1.36 = 18.8A. I'm not sure I'm doing that right, but if so maybe the "switching" question isn't even an issue?
Thanks!
Thanks!