Switching neutral conductor for incoming 120VAC power to UPS unit

Status
Not open for further replies.

Dale001289

Senior Member
Location
Georgia
I have vendor drawings showing a 120VAC, double pole CB for incoming power to a UPS. The breaker is switching both the hot and neutral conductors. In the IEC world its done quite a bit, but I've never seen it in the US. Does the NEC address this?
 
Yes. The neutral may be opened by a device that simultaneously opens all ungrounded lines.
 
In general the NEC prohibits switching or interrupting the neutral, but permits such when all the hot conductors are also interrupted.

I recall that for gasoline pumps, it is required to interrupt both hot and neutral.

Jon
 