Dealing with a conflict of opinion. Does the NEC state that the neutral cannot be switched except in auto. transfer systems? I believe that it does but can't find where in the NEC.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Switching Neutrals

You can switch the neutral if you switch the ungrounded conductors at the same time.

Why you would want to I have no idea, other than a transfer switch.
 

charty

Member
Re: Switching Neutrals

Iwire,
there was a very good reason to do that but i cannot recall what it was. maybe someone else would know.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Switching Neutrals

johnp I just saw your other post about switching the neutral on motor starters.

I do not believe 404.2(B) applies to this as it is common practice.

[ December 17, 2003, 06:05 PM: Message edited by: iwire ]
 

bennie

Esteemed Member
Re: Switching Neutrals

I understand the neutral must be disconnected in the emergency shut off for gasoline dispensers.
 