Hello, in a regulation of my country about electrical installations it says overvoltages can be avoided by
" avoiding switching off no-load transformers circuits from two sides"
does it make sense for you? or is there any possibility that this phrase tries to tell something alike...
 

rcwilson

Senior Member
Location
Redmond, WA
Does it mean avoid ferro-resonance of three-phase connected transformers by using a three-phase switch or breaker to open the circuit? On some designs of transformers, disconnecting one phase at a time can cause ferro-resonance that creates overvoltages.

Otherwise, I don't understand the comment.
 

jghrist

Senior Member
Hello, in a regulation of my country about electrical installations it says overvoltages can be avoided by
" avoiding switching off no-load transformers circuits from two sides"
does it make sense for you? or is there any possibility that this phrase tries to tell something alike...

I'd try to find a copy of the regulation written in the writer's native language.
 