Symetrical Components
mull982
Hello
Can anyone provide and explanation or references explaining what the difference between positive, negative, and zero sequence components are? I have been reviewing a short circuit study, and wanted to know what these components were, and how they were used. Can anyone help?
Thanks
Mull982
mull982 said:
Hello
Thanks
Mull982
SHHHHH (make sure nobody is looking) Here is a closely guarded link that graphically allows you to quickly understand (in 10 minutes or less) all about these components plus lots of other neat stuff.
I only wish this was available earlier.
http://www.powerstandards.com/PQTeachingToyIndex.htm
Let me know ,if this helps.
Good Luck
This was the subject of a graduate level course that I took during my masters degree program. I might give you a notion of what the terms mean, but I can?t teach you how to use them, or at least not without getting a serious case of carpal tunnel syndrome.
To start with, we tend to presume that all loads are balanced among the three phases. That allows us to use simple methods of adding loads. If the loads are not balanced, the math becomes very tricky. If you look at a non-balanced fault (e.g., single line to ground, line to line, or double line to ground, anything other than a bolted three phase fault), the math is also very tricky.
But some brilliant guy (who, by the way, I understand was awarded a PhD on the basis of about 20 pages of hand-written text), came up with a simple way to model unbalanced loads (including unbalanced faults). He created a model that uses three sets of data. One set of data (meaning current and voltage data) would be balanced within itself, and would have the same phase sequence (A-B-C) as the original (unbalanced) load. The second set of data (again meaning current and voltage data) would also be balanced within itself, but it would have the opposite phase sequence (A-C-B). Those two sets of data are called the positive sequence and the negative sequence. The third set of data is also balanced within itself, but there is no phase sequence. All three of its voltages are in phase with each other, as are all three of its currents.
What you are left with are three simple problems, instead of one complex one. You begin the analysis by converting the unbalanced problem into three balanced problems. Then you do the three problems separately. Finally, you combine them back by converting to a single set of data. The mathematical tool used to perform these manipulations is matrix algebra.
There. That?s about all my wrists can handle for now. Did this help?
mull982 said:
Hello
Thanks
Mull982
As Charlie said this is a complex subject. If you care to, this is an attempt
to discuss symmetrical components .
http://www.selinc.com/techpprs/6066.pdf
Thanks for all of the information guys it is all a great help and I have a much better understanding of them now. I remember touching on this subject back as an undergrad but never really grasped the full concept. I am clear now on the concept on what they are used for, now I just have to figure out how to use them which I'm sure is the difficuit part.
Thanks A lot
Mull982