beedubyuh
Member
- Location
- Virginia, USA
We are performing an AC voltage drop test across the field windings of a synchronous motor. The windings are two parallel circuits fed from the same external DC source (through collector rings and brushes). The rotor is composed of 14 salient poles (7 poles per circuit). During the test the rotor is installed in the motor. The expected result when applying 120 Vac, 60 Hz to an individual field circuit is 17.1 Vac drop across each coil (+/- 10%). There are no reports of excessive vibrations when the motor is operating which would further indicate shorted field windings.
Actual voltage drops vary greatly from average:
Circuit 1 (coils 1,2, 5, 6, 9, 10, 13): 14.3, 10.1, 6.4, 24.3, 8.4, 14.8, 24
Circuit 2 (coils 3, 4, 7, 8, 11, 12, 14): 19.6, 29.2, 6.1, 7.4, 27.5, 32.5, 6.5
Could the position of the rotor poles in relation to the stator iron affect individual pole voltage drops (maybe due to inconsistent reluctance paths)? Or is this actually an indication of a failing rotor/shorted field windings?
Actual voltage drops vary greatly from average:
Circuit 1 (coils 1,2, 5, 6, 9, 10, 13): 14.3, 10.1, 6.4, 24.3, 8.4, 14.8, 24
Circuit 2 (coils 3, 4, 7, 8, 11, 12, 14): 19.6, 29.2, 6.1, 7.4, 27.5, 32.5, 6.5
Could the position of the rotor poles in relation to the stator iron affect individual pole voltage drops (maybe due to inconsistent reluctance paths)? Or is this actually an indication of a failing rotor/shorted field windings?