System Bonding Jumper at Transformer

Status
Not open for further replies.

Gategator37

Senior Member
The electrician used a Main Bonding Jumper from the Neutral Conductor to the Grounding Electrode System located in the 112.5 Transformer. This is all fine and dandy; however, at the neutral bar (at transformer) he also landed his EGC's from the primary and secondary panelboards. Is this installation ok, or should he of attached the EGS's to the Ground Bar located at the Transformer. I don't know if the only thing that can attach to the neutral is the "bonding Jumper".

Thanks in advance for your input.
 
As long as there is no "weak link in the chain" with wire size, I don't think it would make any difference as they are all connected together.
 