System Bonding Jumper Size for Parallel Conductors on SDS

Status
Not open for further replies.

Tom91011

Member
I have a separately derived system with a 16kV-480Y277V, 2500kVA transformer. The secondary is connected to a 480V Switchboard Main Breaker approximately 150 feet away. The secondary connection is made up of seven 5-inch PVC Sch 40 conduits, each containing three 750kcmil Cu THHN phase conductors and one 750kcmil Cu THHN neutral conductor.

The neutral conductor will be grounded at one point at the transformer neutral (like Exhibit 250.13 in the Handbook). I am trying to size the system bonding jumper conductors that will run in the conduits with the phase and neutral conductors.

According to 250.102 (C) in the 2005 NEC, I have taken 12.5% of the 7 750kcmil conductors to get the size of the system bonding jumper: 0.125 * 7 * 750 = 656.25 kcmil. I interpret the last two sentences of 250.102 (C) to mean that this is the total cross-section required, and that I can run a bonding jumper in each conduit sized for the conductors in that conduit - this would work out to a 1/0 in each conduit, but the minimum size per 250.66 is 2/0. Is this the correct interpretation or do I need to run a 750 (the next size up from 656) in each conduit for the system bonding jumper?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Welcome to the Forum.
My take, based on 250.30(A)(2) and referenced 250.102(C) would be a 1/0 in each conduit.
I fail to see your the basis of your comment:"minimum size per 250.66 is 2/0", but I may be overlooking something.

Apparently the transformer is outside of the building. You might want to read http://forums.mikeholt.com/showthread.php?t=127208 as you may be able to use your neutrals and bond at the panel and the transformer.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Welcome to the Forum.
My take, based on 250.30(A)(2) and referenced 250.102(C) would be a 1/0 in each conduit.
I fail to see your the basis of your comment:"minimum size per 250.66 is 2/0", but I may be overlooking something.

Apparently the transformer is outside of the building. You might want to read http://forums.mikeholt.com/showthread.php?t=127208 as you may be able to use your neutrals and bond at the panel and the transformer.

These are copper conductors Gus. That would be 2/0 as per 250.66.... Yes/NO
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Yes... :)
Thank you for your diligence...
It's been a long day on a HOTTTT job :)
(that sounds better than I'm older than dirt and can't focus)
View attachment 4808
 

Tom91011

Member
Thank you both for your responses - I got confirmation from some other sources as well - this helped a great deal.

Nice to be a participant in the forum!
 