My question is with regards to the installation of a generator, but I think the same question could apply to any separately derived system.
My generator is rated at 1000KVA. I sized the system bonding jumper at 250kcmil using table 250.102(C)(1) (x3 parallel 600kcmil phase conductors).
I sized the grounding electrode conductor at 3/0AWG using table 250.66.
It seems odd to me that the system bonding jumper must be sized larger than the grounding electrode conductor given that these two conductors essentially form a series circuit between the neutral of the generator and the grounding ring system. Is there a code provision that I am missing, or a reason for the for the larger system bonding jumper size that I am not considering? Is this just the way it is and should I stop questioning it?
Thank you in advance!
2023 NEC
3 600 kcmil conductors x 3 = 1800 kcmil, this exceeds the copper rating of "...over 1100 kcmil.." found in the copper column as noted in T.250.102 (C) (1).
Because the 1100 kcmil exceeds the....over 1100.... The table footnote number 1 says when you exceed that rating (1100 ) the grounded
conductor( neutral ) or bonding jumper shall have an area not less than 12 1/2 % (0.125 ) of the ....equivalent area for parallel supply conductors.
Thus......3 600 kcmil x 3 = 1800 kcmil, 1800 x 0.125 = 225 kcmil. Proceed to Chapter 9 and T.8
Conductors and find the circular mils area greater than 225 kcmil which would be a 250 kcmil conductor. That is also the size of your bonding jumper, too.
You don't need a ground rod.
Check the caption at the top of T.250.102(C), it is for sizing neutral (grounded) and MBJ and system BJ and SSBJ.
It is for conductors as small as 2 AWG or smaller and through size 1100 copper or 1750 aluminum, then you have to apply the 12 1/2 %.
The grounding electrode conductor was selected from T.250.66. There, you max out at a 3/0 copper, there's no 12 1/2% to consider.
A 1,000 KVA generator is an extremely large generator. 1,000KVA x 1,000 = 1,000,000 VA. Assuming the voltage is a standard 4160 voltage and 3 phase of course ......4160 volts x 1.732 = 7205 that's a three phase divider to find the amps.
1,000,000 VA / 7205 = 139 amps. T.450.3(A). For primary protection (OCPD) and not more than 6% impedance and in a unsupervised location and using a fuse rating of 300% would be....139 amps x 300 % = 417 amp fuse.
T.450.3(A) and note number 1 allows for a next size up and T.240.6 (A) List a 450 amp to be
permitted.
It is under the 800 amp rule found in240.(B) (1)(2)(3). This is for the primary side only and not the secondary side.
Thanks for reading
Comments accepted
TX + MASTER #4544
My question is with regards to the installation of a generator, but I think the same question could apply to any separately derived system.
My generator is rated at 1000KVA. I sized the system bonding jumper at 250kcmil using table 250.102(C)(1) (x3 parallel 600kcmil phase conductors).
I sized the grounding electrode conductor at 3/0AWG using table 250.66.
It seems odd to me that the system bonding jumper must be sized larger than the grounding electrode conductor given that these two conductors essentially form a series circuit between the neutral of the generator and the grounding ring system. Is there a code provision that I am missing, or a reason for the for the larger system bonding jumper size that I am not considering? Is this just the way it is and should I stop questioning it?
Thank you in advance!