I would like to know where in article 250 does it say that a panel enclosure can carry a ground fault current to the neutral so the fault current can get back to the source winding to trip the ocpd? Example: I have a separately derived system (transformer) where the case is connected to the gec. Only. The xo is floated. The panel which is the first disconnecting means has a neutral to case connection (a wire sized correctly). The egc is connected via bus bar to the gec. If there is a line side groundfault then it has to travel on the gec then travel on the can to get back to the source. It seams to me that the can is the system bonding jumper because it connects the system grounded conductor to the egc and the gec.