If the poles and pole mounted transformers are located outside, owned by the company I work for but NOT utility and is away from building served, then how to I know if the transformer has the system bonding jumper between grounded conductor and supply side bonding jumper to metal of transformer as well as grounding conductor terminal?
With this being the case I would not normally install a system ground connector in first disconnect/ breaker switch panel. I believe code would allow me to if grounded conductor from transformer was being used as both supply side bonding jumper and grounded conductor neutral, and a parallel path for neutral current was not allowed
With this being the case I would not normally install a system ground connector in first disconnect/ breaker switch panel. I believe code would allow me to if grounded conductor from transformer was being used as both supply side bonding jumper and grounded conductor neutral, and a parallel path for neutral current was not allowed