System Ground Raceway

Status
Not open for further replies.

nivram2

New member
Location
New York, NY
In running a system ground between a Service Switch Ground and building steel, assuming the ground conductor is

uninterrupted, can a large pull box containing other feeders etc. be used as part of the raceway between Building Steel

and the Service Switch Ground.
 
Are we talking about the grounding electrode conductor? If so then yes it can be run with other conductors however make sure the conduit, assuming ferrous metal, is bonded
 
system "ground" is not an NEC term.
Are you referring to the:
Bonding Jumper
GEC
EQG

we get confused on grounding as we don't use the correct terms.
 