Grounding question ex.:
2000AA Pad mounted xfmr.
Substation located in building (remote) with 3200AF/3000AT main circuit breaker.
Phase conductors:
8-sets of 3#600kcmil+grd.
Ground to be sized based 250.66
If the conductors are larger than 1100kcmil copper and the system bonding jumper is not located at the source, the size is based on 12.5% of the area of the largest derived phase conductor. In this cas the largest derived phase conductor would be 600,000*8? = 4,800,000 so 12.5% would be 600,000 now do you divide that by 8 to get the size per set of conductors? It would be the equevlant of each raceway containing a conductor of 75,000cmills that would be a #1 but since a 1/0 is the smallest you can parallel than a 1/0 ground minimum would need to be installed with each set of phase conductors. Is this correct??
I have also seen medium voltage installation where the ground is a 600V ground is this acceptable??
2000AA Pad mounted xfmr.
Substation located in building (remote) with 3200AF/3000AT main circuit breaker.
Phase conductors:
8-sets of 3#600kcmil+grd.
Ground to be sized based 250.66
If the conductors are larger than 1100kcmil copper and the system bonding jumper is not located at the source, the size is based on 12.5% of the area of the largest derived phase conductor. In this cas the largest derived phase conductor would be 600,000*8? = 4,800,000 so 12.5% would be 600,000 now do you divide that by 8 to get the size per set of conductors? It would be the equevlant of each raceway containing a conductor of 75,000cmills that would be a #1 but since a 1/0 is the smallest you can parallel than a 1/0 ground minimum would need to be installed with each set of phase conductors. Is this correct??
I have also seen medium voltage installation where the ground is a 600V ground is this acceptable??