We have low voltage smoke detect in t-bar ceiling, EMT is ran close to each outlet then we are connecting FMC to EMT . FMC is far less then 6' in lengths. Can i use 348.30 exception No.4. Lengths not exceeding 6' from the last strap within accessible ceiling. The last strap is on the EMT just before the transition to FMC