T312.6(B) clarification

Status
Not open for further replies.

CPV_EE

Member
Location
San Diego
Occupation
Electrical Engineer
Having some trouble interpreting the table for 312.6(B).

Do the dashed lines mean the conditions are outside the scope of the standard, is it not allowed, or are the values piggybacked from column 1?

Thanks!


HoVZrua.png
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not allowed because the multiple wires per terminal would indicate parallel conductors which cannot be smaller than #1/0. That is why for more than one conductor the table begins at #1/0.

Welcome to the Forum.
 

CPV_EE

Member
Location
San Diego
Occupation
Electrical Engineer
Not allowed because the multiple wires per terminal would indicate parallel conductors which cannot be smaller than #1/0. That is why for more than one conductor the table begins at #1/0.

Welcome to the Forum.


Much appreciated. Thank you!
 