T312.6(b)

Status
Not open for further replies.

rgiraldo

Member
Location
FL
On table 312.6(B), Note 2 states that "bending space shall be permitted to be reduced by the following number of millimeters".

If I am looking at 250 kcmil with only one wire and in the column for one wire in inches says 8-1/2. Right next to that number is a letter (d). If I look a note 2 at the letter d that alloys me to size down 2 inches the correct bending space would be 6-1/2


Thanks for your help guys..
 