T450.3(A)
Can someone explain the correlation between the "Transformer Rated Impedance" column and the two "Primary Protection Over 600 Volts" columns?
For example: A transformer in a supervised location with rated impedance of 5% can fall under the "Any" impedance of row three, or the "Not more than 6%" impedance of row four.
T450.3(B)
The last sentence of Note 2 states,"If both breakers and fuses are utilizied as the overcurrent device, the total of the device ratings shall ot exceed that allowed for fuses."
The problem is, this table does not distinguish between fuses and circiut breakers.
Appreciate the help
Brian Dolan
Palos Park, IL
T450.3(B)
Appreciate the help
Brian Dolan
Palos Park, IL