T8 battery backup ballasts

Status
Not open for further replies.

Davebones

Senior Member
Having to install some emergency lighting in a furnace area . We want to use a battery backup for a T8 light . Never wired one of these type ,do they need to be on a night light circuit ? Do they work as advertised , 90 min ?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
The unit equipment must be supplied by an unswitched circuit. Also be aware that if this is an emergency light in compliance with Article 700, the circuit that supplies the unit equipment must be the same circuit that supplies the normal area lighting. (Check out 700.12(F))

Chris
 

USMC1302

Senior Member
Location
NW Indiana
Depending on your occupancy, you might think about how the emergency back-up is tested. I've seen lay-in fixtures where the EC has remoted a box with the test switch so the fire marshal and owner's personnel can test them easily. Any way to suggest ease of use might make you some extra money.
 

stevebea

Senior Member
Location
Southeastern PA
Having to install some emergency lighting in a furnace area . We want to use a battery backup for a T8 light . Never wired one of these type ,do they need to be on a night light circuit ? Do they work as advertised , 90 min ?

Google Bodine. Thats what we are using in the office at our shop. They are about 8 years old. I have had to replace a few of them but overall have been satisfied with their preformance. We have 3 lamp troffers with the Bodine on the single lamp and yes they do last 90 min. at reduced wattage.
 