Table 110.31 Compliance

Status
Not open for further replies.

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I'd say no. 110.34 says there shall be clear working space in "the direction of access to live parts" which usually means the front, and sometimes the back. There is also a specific note in the exception that states what rear clearance needs to be if it's required for access to non-electrical parts.

And since switchgear is normally made to be installed in a line up (side by side sections), I say they are generally designed so side access is not required.
 