Before I break the bad news to our subcontractor, is this correct?
On a 13.8kV 3ph 3W ungrounded system - since ‘voltage to ground’ does not exist, you have to use the full 13.8kV as the “Nominal Voltage to Ground” when applying minimum clear distance per Table 110.34(A).