Looking at this table, you can take a demand of 50% receptacle VA after the first 10,000 VA, but this doesn't apply to the 1 VA / SF allowed using 220.14(K).
Has anyone else made the MISTAKE of taking a demand when using the 1 VA / SF allowance in office buildings, I mean there's going to be a demand on receptacles no matter what right??
For instance, a 50,000 SF office building building would be 50,000 VA of receptacle load, but you're not allowed to take a demand on this according to 220.44 since it only applies if you actually knew the yoke count, but who ever knows that? This make NO SENSE!!! Why can't we take the first 10,000 VA at 100% and 50% of the remaining VA, which would be 30,000 VA demand load.
Has anyone else made the MISTAKE of taking a demand when using the 1 VA / SF allowance in office buildings, I mean there's going to be a demand on receptacles no matter what right??
For instance, a 50,000 SF office building building would be 50,000 VA of receptacle load, but you're not allowed to take a demand on this according to 220.44 since it only applies if you actually knew the yoke count, but who ever knows that? This make NO SENSE!!! Why can't we take the first 10,000 VA at 100% and 50% of the remaining VA, which would be 30,000 VA demand load.