Table 220.55 and real world applications regarding load calcs,

Status
Not open for further replies.

sw_ross

Senior Member
Location
NoDak
The table is based on the premise that you know the nameplate ratings of the ranges, whether an individual dwelling or multi-dwelling.

Realistically how often is that known? Normal practice that has been used in my experience, from apprentice through j-man and master, is to run a 40 or 50 amp circuit and install a 50 and 4-wire receptacle without ever knowing the kW rating of the range.
Granted, if it's a higher end home that has wall mounted ovens and separate cooktops you usually have specific info from GC or architect.

When doing load calcs where you don't have nameplate info, how do you "properly" use the table?

Whether you're using the standard or optional methods calcs are based on nameplate ratings...

I understand how to answer a test question regarding a range Calc, I'm just talking real world scenarios. If you have a 20 unit dwelling are you going to really know the nameplates for all those units? Or are you going to run 20 - 40 amp circuits (receptacles)? And how do you do a load Calc without knowing the nameplates?
 
The table is based on the premise that you know the nameplate ratings of the ranges, whether an individual dwelling or multi-dwelling.

Realistically how often is that known? Normal practice that has been used in my experience, from apprentice through j-man and master, is to run a 40 or 50 amp circuit and install a 50 and 4-wire receptacle without ever knowing the kW rating of the range.
Granted, if it's a higher end home that has wall mounted ovens and separate cooktops you usually have specific info from GC or architect.

When doing load calcs where you don't have nameplate info, how do you "properly" use the table?

Whether you're using the standard or optional methods calcs are based on nameplate ratings...

I understand how to answer a test question regarding a range Calc, I'm just talking real world scenarios. If you have a 20 unit dwelling are you going to really know the nameplates for all those units? Or are you going to run 20 - 40 amp circuits (receptacles)? And how do you do a load Calc without knowing the nameplates?
I believe column C is there for good reason - most ranges fall into the not over 12kW requirement there. Oven and cooktops you probably come up with less demand using other columns though.

Single family with over a 12 kW range but you only accounted for 12 kW - probably doesn't ever cause much trouble unless it is a monster range that is more than typical 30" wide.
 
8kw

8kw

I agree. Most load calcs for typical home I use 8kw, on average, maybe 8.8kw in a CYA scenario, for a standard method load Calc.

In the optional load Calc you're suppose to use nameplate ratings...
Anybody ever have an AHJ call you on your optional load Calc number without knowing a specific nameplate (including nameplates for all appliances- dishwasher, garbage disposal, etc)?
 
Also the max rating is only used when all burners and the oven pre-heat function are on simultaneously.
 