I have a client who originally specified (for the sake of simplicity I'll make up the numbers)... 10 Apartment Free-Standing Range top/Oven combo Appliances rated at 10kW...all to be on a new dedicated feeder riser.
220.55 Column C would have me calculate the Max Demand based on 10 units total at 25kW.
No Prob.
Now, the client would like to revise his kitchen design to instead be 10 WALL OVENS rated at say 5kW and 10 COUNTER COOKTOPS rated at 5kW. The same functions as before with the same total nameplate ratings just split to 2 units each fed by a separate breaker but on the same feeder riser. However now 220.55 says I have to use Column B for TWENTY units, so Demand Factor of 28% (100,000 wats x.28 = 28kW)
Same function, same utilization, same total wattage: one is 25kW or is 28kW.
I know I can use either column for the lowest rating when the units are the same # of units, but am I stuck with 28 now vs 25 or can I STILL option to use 25kW?
220.55 Column C would have me calculate the Max Demand based on 10 units total at 25kW.
No Prob.
Now, the client would like to revise his kitchen design to instead be 10 WALL OVENS rated at say 5kW and 10 COUNTER COOKTOPS rated at 5kW. The same functions as before with the same total nameplate ratings just split to 2 units each fed by a separate breaker but on the same feeder riser. However now 220.55 says I have to use Column B for TWENTY units, so Demand Factor of 28% (100,000 wats x.28 = 28kW)
Same function, same utilization, same total wattage: one is 25kW or is 28kW.
I know I can use either column for the lowest rating when the units are the same # of units, but am I stuck with 28 now vs 25 or can I STILL option to use 25kW?