NEC Annex D Example D4(b)- Multi Family Standard Calculation
There are 20 unit and each unit has electrical range, rated 8,000VA. In the example calculation is 20x8,000= 160,000
So Table 220.55 is not applied here. Can the reason of this be this table is for "Single Family Dwelling" .
If a single family dwelling had 20 ranges with each 8,000 VA, than 28% from table would have been applied.
Table 220.55 CAN NOT BE USED for Multi-Family dwelling feeder calculation, Agree?
There are 20 unit and each unit has electrical range, rated 8,000VA. In the example calculation is 20x8,000= 160,000
So Table 220.55 is not applied here. Can the reason of this be this table is for "Single Family Dwelling" .
If a single family dwelling had 20 ranges with each 8,000 VA, than 28% from table would have been applied.
Table 220.55 CAN NOT BE USED for Multi-Family dwelling feeder calculation, Agree?